Aster,
Please see attached CNP’s suggested edits and let me know if you have any questions.
Regards,
Larisa.
From: Planning Geomagnetic Disturbance Task Force <[log in to unmask]>
On Behalf Of Juricek, Michael
Sent: Wednesday, July 31, 2019 2:41 PM
To: [log in to unmask]
Subject: [External Email] Oncor review Draft Methodology for Assessing GMD Impacts
Aster,
Attached are Oncor’ review and proposed edits.
Thanks,
Mike
From: Planning Geomagnetic Disturbance Task Force [mailto:[log in to unmask]]
On Behalf Of Aster Amahatsion
Sent: Tuesday, July 30, 2019 9:28 AM
To: [log in to unmask]
Subject: Re: Draft Methodology for Assessing GMD Impacts
Importance: High
PGDTF,
I have updated the draft based to address bus protection and let me know your comments, the added paragraph is:,
Bus differential relays protect the bus from internal faults based on Khirchoff’s current law that states the sum of the currents entering a given node must be
equal to the currents leaving that node. During GMD Event the currents including the harmonics into the bus are equal to the currents from the bus and will not affect the differential protection except where primary and secondary current transformers respond
differently to harmonics.
Thanks,
Aster Amahatsion
PGDTF Chair 2019
From: Planning Geomagnetic Disturbance Task Force <[log in to unmask]>
On Behalf Of Bowen, Kenneth
Sent: Monday, July 29, 2019 4:10 PM
To: [log in to unmask]
Subject: [EXTERNAL] Re: Draft Methodology for Assessing GMD Impacts
This is an
EXTERNAL email. STOP. THINK before you CLICK links or OPEN attachments. If suspicious please click the 'Report to Incidents' button in Outlook or forward to
[log in to unmask] from a mobile device. |
Aster,
I suppose I need to watch how I phrase it, when I say we, I meant we (PGDTF), not we (CPS Energy).
J
I was making an assumption that there are no effects from GMD because PGDTF has left it out of the guide, however, it could have just been an oversight. As a voting member of the ROS, I will have a hard time
endorsing this document if it doesn’t give some direction on high-bus diff.
Thank you,
Kenneth Bowen, PE
Manager of Transmission Planning & Operations Engineering
Office: 210.353.4142 | Mobile: 210.288.5437
CPS Energy | MailDrop: 100301 | 145 Navarro, San Antonio, Texas 78205
From: Planning Geomagnetic Disturbance Task Force [mailto:[log in to unmask]]
On Behalf Of Aster Amahatsion
Sent: Monday, July 29, 2019 2:59 PM
To: [log in to unmask]
Subject: [InternetMail]Re: Draft Methodology for Assessing GMD Impacts
EXTERNAL EMAIL:
Do not click any links or open any attachments unless you trust the sender and know the content is safe. |
Kenneth,
Yes you can add a section about high bus protection.
Thanks,
Aster
From: Planning Geomagnetic Disturbance Task Force <[log in to unmask]>
On Behalf Of Bowen, Kenneth
Sent: Monday, July 29, 2019 3:46 PM
To: [log in to unmask]
Subject: [EXTERNAL] Re: Draft Methodology for Assessing GMD Impacts
This is an
EXTERNAL email. STOP. THINK before you CLICK links or OPEN attachments. If suspicious please click the 'Report to Incidents' button in Outlook or forward to
[log in to unmask] from a mobile device. |
Aster,
Just a quick question of whether we can add a subsection in Section 5 to speak to high-bus protection, even if it’s just to say that high-bus diff relays won’t be effected by GMD.
Thank you,
Kenneth Bowen, PE
Manager of Transmission Planning & Operations Engineering
Office: 210.353.4142 | Mobile: 210.288.5437
CPS Energy | MailDrop: 100301 | 145 Navarro, San Antonio, Texas 78205
From: Planning Geomagnetic Disturbance Task Force [mailto:[log in to unmask]]
On Behalf Of Aster Amahatsion
Sent: Monday, July 29, 2019 2:13 PM
To: [log in to unmask]
Subject: [InternetMail][MARKETING] Draft Methodology for Assessing GMD Impacts
EXTERNAL EMAIL:
Do not click any links or open any attachments unless you trust the sender and know the content is safe. |
PGDTF members,
Attached is the final draft of “Methodology for Assessing GMD Impacts on ERCOT Power Systems” that I will be emailing to ROS for approval in ROS August meeting . From our last meeting section 5.1 is updated and also some formatting. I have
not received any comment from SPWG System Protection Working Group. Please email me if you have any comment by July 31, 2019.
Thanks
Aster Amahatsion
PGDTF Chair 2019
To unsubscribe from the PGDTF list, click the following link:
http://lists.ercot.com/scripts/wa-ERCOT.exe?SUBED1=PGDTF&A=1
To unsubscribe from the PGDTF list, click the following link:
http://lists.ercot.com/scripts/wa-ERCOT.exe?SUBED1=PGDTF&A=1
To unsubscribe from the PGDTF list, click the following link:
http://lists.ercot.com/scripts/wa-ERCOT.exe?SUBED1=PGDTF&A=1
To unsubscribe from the PGDTF list, click the following link:
http://lists.ercot.com/scripts/wa-ERCOT.exe?SUBED1=PGDTF&A=1
To unsubscribe from the PGDTF list, click the following link:
http://lists.ercot.com/scripts/wa-ERCOT.exe?SUBED1=PGDTF&A=1
Confidentiality Notice: This email message, including any attachments, contains or may contain confidential information intended only for the addressee. If you are not an intended recipient of this message, be advised that any reading,
dissemination, forwarding, printing, copying or other use of this message or its attachments is strictly prohibited. If you have received this message in error, please notify the sender immediately by reply message and delete this email message and any attachments
from your system.
To unsubscribe from the PGDTF list, click the following link:
http://lists.ercot.com/scripts/wa-ERCOT.exe?SUBED1=PGDTF&A=1
***** This email is from an external sender outside of the CenterPoint Energy network. Be cautious about clicking links or opening attachments from unknown sources. *****
To unsubscribe from the PGDTF list, click the following link:
http://lists.ercot.com/scripts/wa-ERCOT.exe?SUBED1=PGDTF&A=1