Larisa extracted the following information from the NERC Application Guide.


Shunt Devices
The bulk power system generally uses two types of shunt elements to help control system voltage: shunt capacitors and shunt reactors. Shunt capacitors present very high impedance to the flow of GIC, and are consequently excluded in the dc analysis. Shunt reactors connected directly to the substation bus or transmission lines, on the other hand, can provide a low impedance path for GIC and should be included in the analysis. The dc model of a grounded-wye shunt reactor is the same as that of a grounded-wye winding of a GSU. If dc winding resistance values are unknown, they can be estimated using an assumed X/R ratio. Note that X/R ratio of a typical dead-tank shunt reactor can be far greater than the X/R ratio of a typical transformer of the same MVA rating. It is not uncommon for the X/R ratio of large shunt reactors to exceed 1000.


The preceding calculation methods use two particular assumptions in order to simplify the calculations: 1) the magnetic field variations are uniform over the area of the power system and 2) the earth conductivity structure only varies with depth (i.e., there are no lateral variations in conductivity). To improve the accuracy of the calculated geoelectric fields both the structure of the source magnetic field and the lateral variations in conductivity should be considered.

Regards,


Michael Juricek, P.E.

Chairman Planning Geomagnetic Disturbance Task Force



Asset Planning Distribution and Transmission
Oncor Electric Delivery Co LLC
E-mail: [log in to unmask]<mailto:[log in to unmask]>
Office: 214.743.6671
Mobile: 214.490.0748

Confidentiality Notice: This email message, including any attachments, contains or may contain confidential information intended only for the addressee. If you are not an intended recipient of this message, be advised that any reading, dissemination, forwarding, printing, copying or other use of this message or its attachments is strictly prohibited. If you have received this message in error, please notify the sender immediately by reply message and delete this email message and any attachments from your system.

########################################################################

To unsubscribe from the PGDTF list, click the following link:
http://lists.ercot.com/scripts/wa-ERCOT.exe?SUBED1=PGDTF&A=1


ATOM RSS1 RSS2